Use a standard browser to make the communication settings for the FP-I4C unit.
This task includes the following steps:
Make the physical connection
Configure the FP‑I4C unit's RS232 COM1 interface to the FP0R PLC
Enable COM2 RS485/RS232 for communication with the KW9M power meters
Enable COM4 ETHERNET for communication with the KW2M power meters
Connect your PC to the FP‑I4C unit and set the IP address of the PC, e.g. 192.168.0.10 (see "Related topics"). The PC must be on the same subnet as the FP‑I4C unit.
Because we are using static IP addresses, connect the LAN cable to the ETH1 connector of the FP‑I4C unit.
Open your browser and enter the URL https://192.168.0.1/fp_config.
Depending on your browser, an insecure connection warning may be displayed. Follow the instructions in your browser to accept the connection. You will then be forwarded to the Web interface of the FP‑I4C unit.
Go to COM1 RS232. and enable
Keep the default settings (Protocol: MEWTOCOL, Autobaud: Enabled, Baud rate: 115200, Parity: Odd, Timeout: 2000).
Enable COM2 RS485/RS232.
Make the following settings (keep the default settings for all other parameters):
Protocol: MEWTOCOL
Autobaud: Disabled (only PLCs can respond to status requests)
Baud rate: 19200
Enable COM4 ETHERNET.
Make the following settings:
Protocol: MODBUS
Timeout: 2000
IP address: 192.168.0.0
Port: 502
Address offset: Enabled and set to 0
Save your configuration.