Memory area for FP0/FP0R expansion units

Use the addresses in this memory area when the FP-I4C unit is used together with FP0/FP0R expansion units.

The FP0/FP0R PROFINET DP slave unit (FP0DPS2D) cannot be used together with the FP-I4C unit.

Memory areas that cannot be written to are marked read-only.

Address

Description

Read-only

33024 (16#8100)

Expansion unit 1: Number of inputs (8/16/32 bits)

33025 (16#8101)

Expansion unit 1: Number of outputs (8/16/32 bits)

33026 (16#8102)

Expansion unit 1: Number of communication errors

33027 (16#8103)

Expansion unit 1: Number of multiplex loops (0: unknown, 1: normal mode, 2: 4-channel mode, 3: 6-channel mode, 4: 8-channel mode)

33028 (16#8104)

Expansion unit 2: Number of inputs (8/16/32 bits)

33029 (16#8105)

Expansion unit 2: Number of outputs (8/16/32 bits)

33030 (16#8106)

Expansion unit 2: Number of communication errors

33031 (16#8107)

Expansion unit 2: Number of multiplex loops (0: unknown, 1: normal mode, 2: 4-channel mode, 3: 6-channel mode, 4: 8-channel mode)

33032 (16#8108)

Expansion unit 3: Number of inputs (8/16/32 bits)

33033 (16#8109)

Expansion unit 3: Number of outputs (8/16/32 bits)

33034 (16#810A)

Expansion unit 3: Number of communication errors

33035 (16#810B)

Expansion unit 3: Number of multiplex loops (0: unknown, 1: normal mode, 2: 4-channel mode, 3: 6-channel mode, 4: 8-channel mode)

33040 (16#8110)

Data input word 1 (16-bit raw value) from expansion unit 1

For analog inputs, the data contains the converted digital value. For digital inputs, the data contains the digital input data. If a unit with 32 inputs is connected, use this address together with the next address for data input word 2.

33041 (16#8111)

Data input word 2 (raw value, 16-bit data) from expansion unit 1

For analog inputs, the data contains the converted digital value. For digital inputs, the data contains the digital input data.

33042 (16#8112) to 33049 (16#8119)

Data input word 1 to data input word 8 (16-bit demultiplexed value) from expansion unit 1

Demultiplexed values are only required for units with more than 32 inputs (e.g. FP0R analog input unit AFP0R-AD4/AD8 with 4 and 8 analog inputs).

33050 (16#811A)

Data output word 1 (16-bit raw value) from expansion unit 1

For analog data, write the converted digital value to this output. For digital data, set the corresponding bits (e.g. write 16#0003 to turn output 0 and 1 to TRUE).

 

33051 (16#811B)

Data output word 2 (16-bit raw value) from expansion unit 1

For analog data, write the converted digital value to this output. For digital data, set the corresponding bits (e.g. write 16#0003 to turn output 0 and 1 to TRUE).

 

33056 (16#8120)

Data input word 1 (16-bit raw value) from expansion unit 2

For analog inputs, the data contains the converted digital value. For digital inputs, the data contains the digital input data. If a unit with 32 inputs is connected, use this address together with the next address for data input word 2.

33057 (16#8121)

Data input word 2 (16-bit raw value) from expansion unit 2

For analog inputs, the data contains the converted digital value. For digital inputs, the data contains the digital input data.

33058 (16#8122) to 33065 (16#8129)

Data input word 1 to data input word 8 (16-bit demultiplexed value) from expansion unit 2

Demultiplexed values are only required for units with more than 32 inputs (e.g. FP0R analog input unit AFP0R-AD4/AD8 with 4 and 8 analog inputs).

33066 (16#812A)

Data output word 1 (16-bit raw value) from expansion unit 2

For analog data, write the converted digital value to this output. For digital data, set the corresponding bits (e.g. write 16#0003 to turn output 0 and 1 to TRUE).

 

33067 (16#812B)

Data output word 2 (16-bit raw value) from expansion unit 2

For analog data, write the converted digital value to this output. For digital data, set the corresponding bits (e.g. write 16#0003 to turn output 0 and 1 to TRUE).

 

33072 (16#8130)

Data input word 1 (16-bit raw value) from expansion unit 3

For analog inputs, the data contains the converted digital value. For digital inputs, the data contains the digital input data. If a unit with 32 inputs is connected, use this address together with the next address for data input word 2.

33073 (16#8131)

Data input word 2 (16-bit raw value) from expansion unit 3

For analog inputs, the data contains the converted digital value. For digital inputs, the data contains the digital input data.

33074 (16#8132) to 33081 (16#8139)

Data input word 1 to data input word 8 (16-bit demultiplexed value) from expansion unit 3

Demultiplexed values are only required for units with more than 32 inputs (e.g. FP0R analog input unit AFP0R-AD4/AD8 with 4 and 8 analog inputs).

33082 (16#813A)

Data output word 1 (16-bit raw value) from expansion unit 3

For analog data, write the converted digital value to this output. For digital data, set the corresponding bits (e.g. write 16#0003 to turn output 0 and 1 to TRUE).

 

33083 (16#813B)

Data output word 2 (16-bit raw value) from expansion unit 3

For analog data, write the converted digital value to this output. For digital data, set the corresponding bits (e.g. write 16#0003 to turn output 0 and 1 to TRUE).

 

Modified on: 2022-01-11Feedback on this pagePanasonic hotline