EtherNet/IP example: Cyclic communication between FP0H and FP7

FP0H and FP7 PLCs can only read data from each other, and each PLC must be added to the scan list of the other PLC.

To be more flexible in using different PLC addresses for communication, set the parameter Auto Allocation to No. Otherwise, only PLC addresses of the type LD can be used.

EtherNet/IP example

Download  

For communication purposes, no PLC program is required. Nevertheless, the sample programs contain:

Overview: Cyclic communication between FP0H and FP7

Add each PLC to the scan list of the other PLC, and make the data available to the other device.

Data exchange in this example:

Configure the parameter Auto Allocation

  1. Set the PLC type FP0H C32ET/EP or FP07 CPS3RE(S), FP07 CPS31E(S), FP07 CPS4RE(S), FP07 CPS41E(S).

  2. Double-click PLC > System registers > Ethernet.

  3. Double-click EtherNet/IP to open the EtherNet/IP setting window.

  4. Select Setting > EtherNet/IP Basic Configuration... from the menu bar.

  5. In the dialog, select No for Auto Allocation.

Configure cyclic communication between FP0H and FP7

  1. Select the adapter device from the Device List and drag it into the scan list.

  2. Set the IP address of the adapter device.

  3. Configure the data available for reading.

  4. For the adapter device, configure the data to read, ensuring it matches the size of the data available for reading.