Before operating this product, read the safety instructions in the related Operating Instructions.
This product is for industrial use only.
Electrical connections must be made by qualified electrical personnel.
Step-by-step instructions will guide you through connecting a PLC to a MINAS servo driver and setting the most important parameters in the PANATERM configuration software.
The following software is available free of charge.
This link will take you to the Panasonic Industry Co., Ltd. Web site.
Torque control is a control mode to change the motor torque. The torque is controlled by analog signals (e.g. 0 to 10V) at the analog inputs of the servo driver. In addition to a torque signal, a speed limit signal is required to limit the motor speed. There are three different torque control modes (torque commands).
This Quick Start Guide describes torque command 0, which uses analog input 1 and a motor speed limit.
Example
An FP0RA21 analog output unit and a MINAS A6SF servo driver are connected using a DVOP4360V cable. An analog signal of 0 to 10V is sent from the unit to the servo driver. Additional signals, e.g. the servo ready or alarm status of the servo driver can be transmitted via the same cable to the PLC.
It is the customer's responsibility to apply the countermeasures that they consider necessary to comply with current regulations on wiring, safety and reducing EMI.
Do not forget to meet the specifications indicated in the hardware manual for each of the devices being wired. If any specifications in the manual conflict with the information in this document, the manufacturer's manual takes preference.
For detailed information on reducing EMI, please refer to Recommendations for EMC-compliant wiring of servo drivers and motors.
Connect the power supply cable to the XA connector. For a 1-phase power supply of 230V, connect a 2-wire cable to the servo driver as illustrated. The L2 pin is not used in 1-phase mode.
Connect the motor cable to the XB connector. The wires are labeled with the letters U, V, and W. Do not change the sequence of the motor phases, e.g. by connecting V to W.
Connect the encoder cable to the X6 connector.
Connect the connection cable to the X4 connector to the analog output unit.
The servo driver is configured using the PANATERM configuration software . Use a commercially available USB A to mini-B cable to connect the PC to the servo driver.
For torque control, the X4 connector of the MINAS A5/A6 servo driver is equipped with an analog input which has a resolution of 16 bits. The voltage range is 0V to +/-10V. The analog input is highlighted in the wiring diagram.
In our example, we will use the following signal inputs and outputs:
SRV-ON (pin 29)
Servo-on input to energize the servo motor.
COM+ (pin 7)
Common input for the power supply of the control signals.
SPR/TRQR/SPL (pins 14–15)
Analog torque command input.
S-RDY (pins 34–35)
Servo-ready output to indicate the ready state of the servo driver.
ALM (pins 36–37)
Servo-alarm output
AT-SPEED (pins 38–39)
Speed attainment output which turns on when the speed specified with Pr4.36 is reached.
Please refer to the Operating Instructions of your MINAS A5/A6 servo driver to learn more about the signal inputs and outputs which might be useful for your application.
Use the PANATERM configuration software to configure the MINAS servo driver.
The following table shows the setting range and description of the basic parameters.
Parameter |
Range |
Description |
---|---|---|
Pr0.01 |
0 to 6 |
Control mode |
Pr3.17 |
0 to 2 |
Torque command input |
Pr3.18 |
0 to 1 |
Torque command direction |
Pr3.19 |
10 to 100 [0.1V/100%] |
Input gain of torque command |
Pr3.20 |
0 to 1 |
Inversion of torque command input |
Pr3.21 |
0 to 20000 [ms/(1000r/min)] |
Speed limit value 1 |
Pr4.22 |
-27888 to 27888 LSB (MINAS A5) -5578 to 5578 LSB (MINAS A6F) |
Analog input 1 offset |
Pr4.23 |
0.00 to 64.00 [ms] (MINAS A5, MINAS A6F) |
Analog input 1 filter |
Pr4.36 |
10 to 20000 [r/min] |
Speed attainment |
PANATERM parameter: Control mode setting
Setting range: 0 to 6
Select 2: Torque control
PANATERM parameter: Torque command selection
Setting range: 0 to 2
PANATERM parameter: Torque command direction designation selection
Setting range: 0 to 1
PANATERM parameter: Torque command input gain
Setting range: 10 to 100 [0.1V/100%]
Set a gain factor for the motor torque based on the voltage applied at the torque command input TRQR. For example, a setting value of 30 results in a torque of 100% for an input voltage of 3V.
PANATERM parameter: Torque command input inversion
Setting range: 0 to 1
PANATERM parameter: Speed limit value 1
Setting range: 0 to 20000
Default value: 0
Specify the speed limit used for torque control.
PANATERM parameter: Analog input 1 (A|1) offset setting
The default value is 0.
Specify an offset value to apply a torque on the motor shaft which compensates for drift.
PANATERM parameter: Analog input 1 (A|1) filter setting
Setting range: 0.00 to 64.00 [ms]
The default value is 0.
This parameter acts like a low-pass filter to produce a stable voltage: the higher the setting value, the longer the delay.
Setting range: 10 to 20000 [r/min]
The default value is 1000r/min.
When the motor speed specified by this parameter is reached, the output AT-SPEED turns on.
For some applications, the software function of physical pins of the servo driver must be changed. Use the PANATERM configuration software to make the pin assignment.