This is a predefined DUT with overlapping elements. The DUT can be used for communication between the PLC and a touch terminal of the GT series.
When you have made settings in GTWIN for the alarm history or defined a group, the alarm history control function becomes available. Select On if you want to use it and then select a register as the control device.
Alarm History tab in GTWIN with control device enabled
The control device helps you monitor group no. 0 and/or group no. 1 and provides the following functions:
start and stop monitoring the alarm history of a group
check whether the memory of a group is full
clear the memory of a group
check whether clearing the memory is completed
save the history of a group to an SD card
check whether the saving of a group to an SD card is completed
The table below explains the bit assignment of the control device.
When a bit is set, the status is TRUE, i.e. the function is executed.
Memory clear
When bit 9 is set to 1, the memory for group no. 1 is full. Clear it by setting bit 1 of byte n+1 (R211 if WR20 is the control device selected) to 1.
Save history in SD card
Save the history of group no. 0 to the SD card by setting bit 4 of byte n (R204 if WR20 is the control device selected) to 1.