F356_Parameters_NonHold_DUT

NOTE

When you execute the instruction for the first time, i.e. when the execution condition specified at Run turns to TRUE, the default values are written to the DUT members 1 to 9 of DUT .

This DUT can be used with the following instruction(s): F356_PID_PWM.

This DUT specifies the manipulated value (MV) and the control parameters (4 words).

MV (INT)

Stores the manipulated value (output value)

Default value 0

Setting range -10000–10000

LowerLimit (INT)

Sets the lower limit of the manipulated value MV

Default value 0

Setting range min. -10000

UpperLimit (INT)

Sets the upper limit of the manipulated value MV

Default value 10000

Setting range max. 10000

PV_Band_WithFullOutput (INT)

No PID control is performed and the output is at 100% until the defined level (0–80%) of the set point value has been reached.

Default value 0

Setting range 0–80%

Ts (INT)

Sets the sampling time for updating the measured input values.

Unit = 0.01s

Also sets the PWM output period.

Default value 100 (1s)

Setting range 1–3000 (0.01–30s)

ControlMode (WORD)
  • 0: Inverse PI-D control, e.g. heating
  • 1: Forward PI-D control, e.g. cooling
  • 2: Inverse I-PD control, e.g. heating
  • 3: Forward I-PD control, e.g. cooling

Default value 0

Setting range 0–3

AT_Bias (INT)

Sets a bias value for performing auto-tuning

Default value 0

Setting range min. 0

AT_Correction_Kp (INT)

Sets the correction value of the auto-tuning result for Kp

Default value 125%

Setting range 50–500%

AT_Correction_Ti (INT)

Sets the correction value of the auto-tuning result for Ti

Default value 200%

Setting range 50–500%

AT_Correction_Td (INT)

Sets the correction value of the auto-tuning result for Td

Default value 100%

Setting range 50–500%

AT_Progress (INT)

Stores the auto-tuning progress

Default value 0

Setting range 0–5

WorkingArea (ARRAY..OF..INT)

Working area of up to 30 words for PID processing and auto-tuning

Default value 0

NOTE

When the execution condition turns to TRUE, the default value is set. The manipulated value MV is only output in the range of the specified upper and lower limit.

Detailed information on the setting method:

Modified on: 2022-03-02Feedback on this pagePanasonic hotline