F173_PulseOutput_PWM_DUT

This DUT can be used with the following instruction(s): F173_PulseOutput_PWM

Elements of the DUT (identifiers):

iFrequencyValue: Frequency and period [hex constant K]
  • Values for FP-Sigma, FP-X

    Resolution of 1000

    Resolution of 100

    K

    Frequency [Hz]

    Period [ms]

    K

    Frequency [Hz]

    Period [ms]

    0

    1.5

    666.7

    20

    15.6 k

    0.06

    1

    2.0

    502.5

    21

    20.8 k

    0.05

    2

    4.1

    245.7

    22

    25.0 k

    0.04

    3

    6.1

    163.9

    23

    31.3 k

    0.03

    4

    8.1

    122.9

    24

    41.7 k

    0.02

    5

    9.8

    102.4

    6

    19.5

    51.2

    7

    48.8

    20.5

    8

    97.7

    10.2

    9

    201.6

    5.0

    10

    403.2

    2.5

    11

    500.0

    2.0

    12

    694.4

    1.4

    13

    1.0 k

    1.0

    14

    1.3 k

    0.8

    15

    1.6 k

    0.6

    16

    2.1 k

    0.5

    17

    3.1 k

    0.3

    18

    6.3 k

    0.2

    19

    12.5 k

    0.1

    NOTE

    FP-XC14T, C30/C60T: When using channel 2 or 3, the maximum value of K is 20.

  • Values for FP0R

    K

    Frequency [Hz]

    Period [ms]

    3

    6

    166.67

    4

    7.5

    133.33

    5

    12.5

    80.00

    6

    25

    40.00

    7

    50

    20.00

    8

    100

    10.00

    9

    200

    5.00

    10

    400

    2.50

    11

    600

    1.67

    12

    800

    1.25

    13

    1000

    1.00

    14

    1200

    0.83

    15

    1600

    0.63

    16

    2000

    0.50

    17

    3000

    0.33

    18

    4800

    0.21

  • Values for FP0H

    Resolution of 1000

    Resolution of 1000

    K

    Frequency [Hz]

    Period [ms]

    K

    Frequency [Hz]

    Period [ms]

    0

    1.5

    666.67

    16

    2000.0

    0.50

    1

    2.0

    500.00

    17

    3000.0

    0.33

    2

    4.0

    250.00

    18

    6000.0

    0.17

    3

    6.0

    166.67

    19

    12500.0

    0.08

    4

    8.0

    125.00

    20

    15000.0

    0.067

    5

    10.0

    100.00

    21

    20000.0

    0.050

    6

    20.0

    50.00

    22

    25000.0

    0.040

    7

    50.0

    20.00

    23

    30000.0

    0.033

    8

    100.0

    10.00

    24

    40000.0

    0.025

    9

    200.0

    5.00

    25

    50000.0

    0.020

    10

    400.0

    2.50

    26

    60000.0

    0.017

    11

    500.0

    2.00

    27

    70000.0

    0.0143

    12

    700.0

    1.48

    Resolution of 100

    13

    1000.0

    1.00

    28

    80000.0

    0.0125

    14

    1300.0

    0.77

    29

    90000.0

    0.0111

    15

    1600.0

    0.625

    30

    100000.0

    0.010

    NOTE

    FP-XC14T, C30/C60T: When using channel 2 or 3, the maximum value of K is 20.

iPulseWidthModulationDuty: Duty ratio (for pulse duration and period) [constant]

The ratio between the pulse duration and the period of a rectangular waveform. For a pulse train in which the pulse duration is 1ms and the pulse period is 4ms, the duty ratio is 0.25 or 25%.

  • Values for FP-Sigma, FP-X

    Values for K < 20: 0-999 (0.0%-99.9%). Values for K ³ 20: 0-990 (0%-99%). Values are specified in units of 1% (steps of 10). Digits behind the decimal point are rounded off.

  • Values for FP0H

    For the control codes K0–K27, setting range: K0–K1000 (0.0%–100.0%)

    For the control codes K28–K30, setting range: K0–K1000 (0%–100%)

Modified on: 2023-02-21Feedback on this pagePanasonic hotline