PID_Work_Area_DUT

NOTE

When you execute the instruction for the first time, i.e. when the execution condition specified at Run turns to TRUE, the default values are written to the DUT members 1 to 9 of DUT .

This DUT can be used with the following instruction(s): FP_PID

Elements of the DUT (identifiers):

MV

Manipulated value, output value [range: -10000–10000, default 0]

LowerLimit

Output lower limit [min. -10000, default 0]

UpperLimit

Output upper limit [max. 10000, default 10000]

PV_Band_WithFullOutput

no pid control and full 100% output if the PV is in this band [range: 0%–80%, default 0%]

Ts

Sampling time in unit 0.01s

  • FP series: [range: 1–3000 (0.01–30s), default 100 (1s)]

  • FP7 series: [range: 1–6000 (0.01–60s), default 100 (1s)]

Control

0: Derivative - Reverse heating (default value)

1: Derivative - Forward cooling

2: Proportional derivative - Reverse heating

3: Proportional derivative - Forward cooling

AT_Bias

Bias value for autotuning [default 0]

AT_Correction_Kp

Correction data of autotuning result Kp in unit % [range: 50%–500%, default 125%]

AT_Correction_Ti

Correction data of autotuning result Ti in unit % [range: 50%–500%, default 200%]

AT_Correction_Td

Correction data of autotuning result Td in unit % [range: 50%–500%, default 100%]

AT_Progress

Auto-tuning progress [range: 0–5, default 0]

WorkingArea1

Working area 1

MV_Internal

Internal value for MV. Can be used to prevent internal overshooting and for manual control

WorkingArea2

Working area 2