Unit_AnalogInput_FP0R_AD4

Function block to read from an FP0R-AD4 unit.

This function block reads converted digital values from the analog input channels of the analog unit. The converted digital values are stored per channel in the output variables iInChannel0 to iInChannel3.

The analog input ranges are also set with this function block.

The number of channels must be set with the DIP switches.

Parameters

Input

iIOWordOffset (INT)

Set the offset of the first WX/WY address of the analog unit according to its installation position.

For analog expansion units connected directly to the CPU (without adapter): Use ExpansionUnitToIOWordOffset_FP0 or make the following settings: 2 (WX2/WY2) for unit number 1, 4 (WX4/WY4) for unit number 2, 6 (WX6/WY6) for unit number 3

For analog expansion units connected to the CPU via an adapter: Use ExpansionUnitToIOWordOffset_FPX_FP0 or select the offset from the table.

Unit position relative to the adapter

Adapter position relative to the CPU

1st unit

2nd unit

3rd unit

4th unit

5th unit

6th unit

7th unit

8th unit

1st unit

30

40

50

60

70

80

90

100

2nd unit

32

42

52

62

72

82

92

102

3rd unit

34

44

54

64

74

84

94

104

wInChannel0_Config to wInChannel3_Config (WORD)

Set the voltage or current range for the analog input channel.

Values:
  • 0: -10 to +10V
  • 1: -5 to +5V
  • 2: 0 to 10V
  • 3: 0 to 5V, 0 to 20mA (depending on wiring method)

Output

iChannel0 to iChannel3 (INT)
Returns the converted digital data from the analog unit by channel.
Values:
  • For -10 to +10V, -5 to +5V: -8000 to +8000
  • For 0 to 10V, 0 to 5 V, 0 to 20mA: 0 to 16000

DIP switch settings

DIP switches 1 and 2 must be ON to use 14-bit mode. DIP switches 3 and 4 are used to set the number of channels, and DIP switch 5 is used to turn averaging on or off.

The DIP switch settings will become effective when the power is turned from OFF to ON.

Number of channels:
 

2 (0 and 1)

4 (0 to 3)

Input averaging:

No averaging: Conversion data is set for the specified input contact point area for each A/D conversion, on each channel.

Averaging: On each channel, for each A/D conversion, the maximum and minimum values from the data of the last ten times are excluded, the data from the other eight times is averaged and the result is set.

 

No averaging

Averaging

Input wiring

Voltage input

Current input

Connect the input instrument between the V and the COM terminal.

Connect the V and the I terminals. Connect the input instrument between the bridge the and COM terminal.

Conversion characteristics

-10V to +10V DC input

-5V to +5V DC input

0V to 5V DC input

Digital value (INT)

Analog value

Digital value (INT)

Analog value

Digital value (INT)

Analog value

-8000

-10V

-8000

-5V

0

0.0V

-4000

-5V

-4000

-2.5V

4000

1.25V

0

0V

0

0V

8000

2.5V

+4000

+5V

+4000

+2.5V

8000

3.75V

+8000

+10V

+8000

+5V

16000

5.0V

0V to 10V DC input

0mA to 20mA input

Digital value (INT)

Analog value

Digital value (INT)

Analog value

0

0.0V

0

0.0mA

4000

2.5V

3200

4.0mA

8000

5.0V

6400

8.0mA

12000

7.5V

9600

12.0mA

16000

10.0V

12800

16.0mA

 

16000

20.0mA

Tip

This command description provides basic hardware documentation only. For detailed technical information, consult the manual:

FP0R Analog I/O Unit User's Manual

Example

POU header

All input and output variables used for programming this function have been declared in the POU header. The same POU header is used for all programming languages.

VAR
	Inst_FP0R_AD4: Unit_AnalogInput_FP0R_AD4;
	iAnalogIn0: INT:=0;
	iAnalogIn1: INT:=0;
	iAnalogIn2: INT:=0;
	iAnalogIn3: INT:=0;
END_VAR

LD body

Use ExpansionUnitNumberToIOWordOffset_FP0 or ExpansionUnitNumberToIOWordOffset_FPX_FP0 to calculate the word offset of the analog unit connected to the CPU.

BODY
    WORKSPACE
        NETWORK_LIST_TYPE := NWTYPELD ;
    END_WORKSPACE
    NET_WORK
        NETWORK_TYPE := NWTYPELD ;
        NETWORK_LABEL :=  ;
        NETWORK_TITLE :=  ;
        NETWORK_HEIGHT := 8 ;
        NETWORK_BODY
B(B_COMMENT,,FP0R-AD4,2,0,17,1,);
B(B_FB,Unit_AnalogInput_FP0R_AD4!,Inst_FP0R_AD4,19,1,34,8,,?BiIOWordOffset?BwInChannel0_Config?BwInChannel1_Config?BwInChannel2_Config?BwInChannel3_Config?CiInChannel0?CiInChannel1?CiInChannel2?CiInChannel3);
B(B_VARIN,,2,17,2,19,4,);
B(B_VAROUT,,iAnalogIn0,34,2,36,4,);
B(B_VARIN,,0,17,3,19,5,);
B(B_VAROUT,,iAnalogIn1,34,3,36,5,);
B(B_VARIN,,0,17,4,19,6,);
B(B_VAROUT,,iAnalogIn2,34,4,36,6,);
B(B_VARIN,,0,17,5,19,7,);
B(B_VAROUT,,iAnalogIn3,34,5,36,7,);
B(B_VARIN,,0,17,6,19,8,);
L(1,0,1,8);
        END_NETWORK_BODY
    END_NET_WORK
END_BODY

ST body

Inst_FP0R_AD4(iIOWordOffset := 2,
	wInChannel0_Config := 0,
	wInChannel1_Config := 0,
	wInChannel2_Config := 0,
	wInChannel3_Config := 0,
	iInChannel0 => iAnalogIn0,
	iInChannel1 => iAnalogIn1,
	iInChannel2 => iAnalogIn2,
	iInChannel3 => iAnalogIn3);

Modified on: 2024-06-21Feedback on this pagePanasonic hotline