FP_MODBUS_MASTER

Write data to slave or read data from slave

Use this instruction to write data from a master to a slave or read data from a slave via the communication port using the Modbus RTU protocol, as defined in the system registers of the port used. Make sure the same protocol is set for master and slave.

Parameters

Input

Port (WORD, INT, UINT)

Specifies the communication ports depending on the PLC type:

  • COM port e.g. SYS_COM0_PORT

  • Ethernet port e.g. SYS_ETHERNET_USER_CONNECTION_1

  • MCU/SCU e.g. 16#xx01 (xx = slot number) in COM01

SlaveAddress (WORD, INT, UINT)

Station number of the slave

  • For FP7 only:

    • Function codes 05, 06, 15, 16: 0–247

      When SCU is used and "0" is specified for the slave unit number, a global transfer is executed. In this case, there is no response message from the slave unit.

    • Function codes 01, 02, 03, 04: 1-247

  • For other PLCs:

    • Function codes 05, 06, 15, 16: 0–99

      When "0" is specified for the slave unit number, a global transfer is executed. In this case, there is no response message from the slave unit.

    • Function codes 01, 02, 03, 04: 1-99

Set to 1, if a SYS_ETHERNET_USER_CONNECTION_xx is applied to input Port

FunctionCode* (WORD, INT, UINT)

SYS_MODBUS_01_READ_COIL

SYS_MODBUS_02_READ_INPUT

SYS_MODBUS_03_READ_HOLDING_REGISTER

SYS_MODBUS_04_READ_INPUT_REGISTERS

SYS_MODBUS_05_FORCE_COIL

SYS_MODBUS_06_PRESET_REGISTER

SYS_MODBUS_15_FORCE_COILS

SYS_MODBUS_16_PRESET_REGISTERS

StartRegister (WORD, INT, UINT)

Starting address (0–65535). The address type depends on the command specified by FunctionCode*.

NumberOfRegisters* (WORD, INT, UINT)

Number of transmission bits or words.

  • 1 for function codes 05, 06

  • 1–2040 for function codes 01, 02

  • 2–2040 for function code 15

  • 1–127 for function codes 03, 04

  • 2–127 for function code 16

MasterData (BOOL, INT, UINT, WORD, DINT, UDINT, DWORD, REAL, DATE, TOD, DT, STRING)

Source address on the master for the data to be written to the slave.

Output

Result (WORD, INT, UINT)

For FP7 only: For a description of all error codes, please refer to the table of Modbus/MEWTOCOL communication error codes.

For other PLCs: set to 0

Time chart

  1.  (1) Master communication clear-to-send flag,e.g. sys_bIsEthernetUserConnection1MasterCommunication
  2.  (2) Check that the master communication clear-to-send flag is TRUE and check that the master communication sending flag is FALSE
  3.  (3) Master communication sending flag, e.g. sys_bIsEthernetUserConnection1MasterCommunicationActive

    While sending: Master communication sending flag is TRUE

    Sending done: Master communication sending flag is FALSE

  4.  (4) Execute this instruction
  5.  (5) Master communication sending done flag, e.g. sys_bIsEthernetUserConnection1CommunicationError

    Normal completion: FALSE

    Abnormal completion: TRUE

  6.  (6) Send data
  7.  (7) Processing of the received response

Error flags

sys_bIsOperationErrorHold (turns to TRUE and remains TRUE)
  • if the area specified using the index modifier exceeds the limit.

  • If slave or master data exceed the available address range.
  • If the communication mode is not set to MEWTOCOL-COM Master/Slave or Modbus RTU Master/Slave.
  • If the COM port selected requires a communication cassette that has not been installed.
sys_bIsOperationErrorNonHold (turns to TRUE for one scan)
  • if the area specified using the index modifier exceeds the limit.

  • If slave or master data exceed the available address range.
  • If the communication mode is not set to MEWTOCOL-COM Master/Slave or Modbus RTU Master/Slave.
  • If the COM port selected requires a communication cassette that has not been installed.

Example

SYS_MODBUS_01_READ_COIL

When you apply this constant to the input parameter FunctionCode*, the corresponding Modbus command is executed.

For the special case that the connected slave is a Panasonic PLC configured as Modbus RTU slave via system register, one or multiple bits are read from:

  • Y (Output)

  • R (Internal flags)

Example

Executing Modbus command 01: reads 1 bit from a Modbus slave beginning at start register 56 set by the variable StartRegister. Then the command stores the 1 bit in the master beginning at the address set by the variable bBool2. The slave's address is converted to a device-specific address depending on the Modbus specifications of the device.

If the connected slave is a Panasonic PLC, the start register 56 corresponds to output Y38 (3*16+8=56).

SYS_MODBUS_02_READ_INPUT

When you apply this constant to the input parameter FunctionCode*, the corresponding Modbus command is executed.

For the special case that the connected slave is a Panasonic PLC configured as Modbus RTU slave via system register, one or multiple bits are read from:

  • X (Input)

Example

Executing Modbus command 02: reads 1 bit from a Modbus slave beginning at start register 66 set by the variable StartRegister. Then the command stores the 1 bit in the master beginning at the address set by the variable bBool2. The slave's address is converted to a device-specific address depending on the Modbus specifications of the device.

If the connected slave is a Panasonic PLC, start register 66 corresponds to input X42 (4*16+2=66).

SYS_MODBUS_03_READ_HOLDING_REGISTER

When you apply this constant to the input parameter FunctionCode*, the corresponding Modbus command is executed.

For the special case that the connected slave is a Panasonic PLC configured as Modbus RTU slave via system register, one or multiple bits are read from:

  • DT (data registers)

Example

Executing Modbus command 03: reads 2 words from a Modbus slave beginning at start register 100 set by the variable StartRegister. Then the command stores the 2 words in the Modbus master 2 beginning at the address set by the variable rCount2. The slave's address is converted to a device-specific address depending on the Modbus specifications of the device.

If the connected slave is a Panasonic PLC, start register 100 corresponds to data register DT100.

Maximum number of registers: 127.

SYS_MODBUS_04_READ_INPUT_REGISTERS

When you apply this constant to the input parameter FunctionCode*, the corresponding Modbus command is executed.

For the special case that the connected slave is a Panasonic PLC configured as Modbus RTU slave via system register, one or multiple bits are read from:

  • WL0–WL127 (Link flags)

  • LD0–LD256 (Link registers)

Example

Executing Modbus command 04: reads 7 words from a Modbus slave beginning at start register 2018 set by the variable StartRegister. Then the command stores the 7 words in the master beginning at LD25 set by the variable MasterData. The slave's address is converted to a device-specific address depending on the Modbus specifications of the device.

If the connected slave is a Panasonic PLC, start register 2018 corresponds to link register LD18.

Maximum number of registers: 127.

SYS_MODBUS_05_FORCE_COIL

When you apply this constant to the input parameter FunctionCode*, the corresponding Modbus command is executed.

In case the connected slave is a Panasonic PLC in Modbus RTU mode, one or multiple bits are written to:

  • Y (Output)

  • R (Internal flags)

Example

Executing Modbus command 05: writes 1 bit to a Modbus slave beginning at address WY1 set by the variable MasterData. Then the command stores the 1 bit in a Modbus slave beginning at start register 35 set by the variable StartRegister. The slave's address is converted to a device-specific address depending on the Modbus specifications of the device.

If the connected slave is a Panasonic PLC, address 35 corresponds to output Y23 (2*16+3=35).

When writing multiple bit data use the SYS_MODBUS_15_FORCE_COILS constant.

Maximum number of register: 1

SYS_MODBUS_06_PRESET_REGISTER

When you apply this constant to the input parameter FunctionCode*, the corresponding Modbus command is executed.

In case the connected slave is a Panasonic PLC in Modbus RTU mode, one or multiple bits are written to:

  • DT (data registers)

Example

Executing Modbus command 06: writes 1 word to a Modbus slave beginning at address DT14 set by the variable MasterData. Then the command stores the 1 word in the Modbus slave beginning at start register 21 set by the variable StartRegister. The slave's address is converted to a device-specific address depending on the Modbus specifications of the device.

If the connected slave is a Panasonic PLC, start register 21 corresponds to data register DT21.

When writing multiple bit data use the SYS_MODBUS_15_FORCE_COILS constant.

Maximum number of register: 1

SYS_MODBUS_15_FORCE_COILS

When you apply this constant to the input parameter FunctionCode*, the corresponding Modbus command is executed.

In case the connected slave is a Panasonic PLC in Modbus RTU mode, one or multiple bits are written to:

  • Y (Output)

  • R (Internal flags)

Example

Executing Modbus command 15: writes 64 bits to a Modbus slave beginning at address WY1 set by the variable MasterData. Then the command stores the 64 bits in the Modbus slave beginning at start register 48 set by the variable StartRegister. The slave's address is converted to a device-specific address depending on the Modbus specifications of the device.

If the connected slave is a Panasonic PLC, address 48 corresponds to output Y30 (3*16=48).

SYS_MODBUS_16_PRESET_REGISTERS

When you apply this constant to the input parameter FunctionCode*, the corresponding Modbus command is executed.

In case the connected slave is a Panasonic PLC in Modbus RTU mode, one or multiple bits are written to:

  • DT (data registers)

Example

Executing Modbus command 16: writes data to a Modbus slave beginning at the address set by the variable rCount1. Then the command stores the data in the Modbus slave 2 beginning with start register 100 set by the variable StartRegister. The slave's address is converted to a device-specific address depending on the Modbus specifications of the device.

If the connected slave is a Panasonic PLC, start register 100 corresponds to data register DT100.

Maximum number of registers: 127.