F177_PulseOutput_Home

Home return

This instruction performs a home return according to the parameters in the specified DUT.Pulses are output from the specified channel when the control flag for this channel is FALSE and the execution condition is TRUE.

Parameters

Input

s_dutDataTable (F177_PulseOutput_Home_Type0_DUT) or (F177_PulseOutput_Home_Type1_DUT)

Starting address of area containing the data table

n_iPulseOutputChannel* (decimal constant)

Pulse output channel:0–3

Remarks

After a drive system has been switched on, there is a difference between the internal position value (elapsed value) and the mechanical position of the axis; this difference cannot be predetermined. The internal value must be synchronized with the actual position value of the axis. This is done by means of a home return, during which a position value is registered at a known reference point (home).During execution of a home return instruction, pulses are continuously output until the home input is enabled. The I/O allocation is determined by the channel used.To decelerate movement when near the home position, designate a near home input and set bit 4 of the special data register storing the pulse output control code (sys_wHscOrPulseControlCode) to TRUE and back to FALSE again.The deviation counter clear output can be set to TRUE when home return has been completed.

Select one of two different operation modes:

  • Type 0:

    The home input is effective regardless of whether or not there is a near home input, whether deceleration is taking place, or whether deceleration has been completed.

    Without near home input:

    1.  (1) Initial speed
    2.  (2) Target speed
    3.  (3) -
    4.  (4) Home input: TRUE

    With near home input:

    1.  (1) Initial speed
    2.  (2) Target speed
    3.  (3) Near home input: TRUE
    4.  (4) Home input: TRUE
    5.  (5) Creep speed
    6.  (6) Home input is effective at any time.
  • Type 1: The home input is effective only after deceleration (started by near home input) has been completed.

    1.  (1) Initial speed
    2.  (2) Target speed
    3.  (3) Near home input: TRUE
    4.  (4) Home input: TRUE
    5.  (5) Creep speed
    6.  (6) Home input is effective only after deceleration

Use the following predefined DUT: F177_PulseOutput_Home_Type0_DUT or F177_PulseOutput_Home_Type1_DUT

The following parameters can be specified in the DUT:

  • Control code

  • Initial speed

  • Target speed

  • Acceleration time

  • Deceleration time

  • Creep speed

  • Deviation counter clear signal (output time)

Pulse output characteristics

  • The pulse output frequency changes according to the specified acceleration time and the specified deceleration time.

  • The difference between target and initial speed determines the slope of the ramps.

  • Pulses are output using a duty of 25%.

  • With the pulse output method "pulse/direction", pulses are output approx. 300ms after the direction signal has been output; the motor driver characteristics are simultaneously taken into consideration.

General programming information

  • Set "Pulse output" for the desired channel in the system registers.

  • Even when home input has occurred, executing this instruction causes pulse output to begin.

  • If the near home input is enabled while acceleration is in progress, deceleration will start.

  • The deviation counter clear signal is allocated to dedicated output numbers specific to each PLC type.

  • If both the main program and the interrupt program contain code for the same channel, make sure both are not executed simultaneously.

  • When a pulse output instruction is executed and pulses are being output, the pulse output control flag (e.g. sys_bIsPulseChannel0Active) of the corresponding channel is TRUE. No other pulse output instruction can be executed as long as this flag is TRUE.

  • When programs are being edited in RUN mode, pulse output stops but resumes after the program changes have been downloaded.

  • We strongly recommend that you incorporate a forced stop option in your positioning program.

  • The status of the high-speed counter control flag or pulse output control flag may change while a scan is being carried out. For example, if the number of received bytes is read more than once different statuses may exist within one scan.

Deviation counter clear outputs and home inputs for FP0R

  • FP0R C16

    Channel no.

    Deviation counter clear output

    Home input

    0 Y6 X4
    1 Y7 X5
    2 X6
    3 X7
    NOTE
    • Inputs X4–X7 can either be used as high-speed counter inputs or as home inputs.

    • Y6 and Y7 can either be used as pulse outputs for channel 3 or as deviation counter clear outputs for channel 0 and 1.

  • FP0R C32, T32, F32

    Channel no.

    Deviation counter clear output

    Home input

    0 Y8 X4
    1 Y9 X5
    2 YA X6
    3 YB X7
    NOTE

    Inputs X4–X7 can either be used as high-speed counter inputs or as home inputs.

Example

Global variables

In the global variable list you define variables that can be accessed by all POUs in the project.

DUT

The DUT F177_PulseOutput_Home_Type1_DUT is predefined in the “FP library”.

POU header

All input and output variables used for programming this function have been declared in the POU header.The same POU header is used for all programming languages.

	VAR_EXTERNAL
		X0_bMotorSwitch: BOOL:=FALSE;
			(*at X0*)
	END_VAR
	VAR 
		diInitialSpeed: DINT:=1000;
		diTargetSpeed: DINT:=5000;
		diAccelerationTime: DINT:=3000;
		diDecelerationTime: DINT:=3000;
		diCreepSpeed: DINT:=5000;
		dutHomeType1: F177_PulseOutput_Home_Type1_DUT:=dwControlCode := 16#0012,
diInitialSpeed := 0,
diTargetSpeed := 0,
diAccelerationTime := 0,
diDecelerationTime := 0,
diCreepSpeed := 0;
			(*For ControlCode (16#0012):
1 = Forward 
2 = Pulse/Sign forward on*)
		@'': @'';
	END_VAR

LD body

BODY
    WORKSPACE
        NETWORK_LIST_TYPE := NWTYPELD ;
        ACTIVE_NETWORK := 0 ;
    END_WORKSPACE
    NET_WORK
        NETWORK_TYPE := NWTYPELD ;
        NETWORK_LABEL :=  ;
        NETWORK_TITLE :=  ;
        NETWORK_HEIGHT := 24 ;
        NETWORK_BODY
B(B_CONTACT,,X0_bMotorSwitch,4,1,6,3,R);
B(B_F,E_MOVE!,Instance,17,4,23,8,,?DEN?D?AENO?C);
B(B_F,E_MOVE!,Instance,17,8,23,12,,?DEN?D?AENO?C);
B(B_VAROUT,,dutHomeType1.diTargetSpeed,23,6,25,8,);
B(B_VARIN,,diTargetSpeed,15,6,17,8,);
B(B_VAROUT,,dutHomeType1.diAccelerationTime,23,10,25,12,);
B(B_VARIN,,diAccelerationTime,15,10,17,12,);
B(B_F,E_MOVE!,Instance,17,20,23,24,,?DEN?D?AENO?C);
B(B_VAROUT,,dutHomeType1.diDeviationCounterClearSignalOutputTime,23,22,25,24,);
B(B_VARIN,,0,15,22,17,24,);
B(B_F,E_MOVE!,Instance,17,0,23,4,,?DEN?D?AENO?C);
B(B_VAROUT,,dutHomeType1.diInitialSpeed,23,2,25,4,);
B(B_VARIN,,diInitialSpeed,15,2,17,4,);
B(B_F,E_MOVE!,Instance,17,12,23,16,,?DEN?D?AENO?C);
B(B_VAROUT,,dutHomeType1.diDecelerationTime,23,14,25,16,);
B(B_VARIN,,diDecelerationTime,15,14,17,16,);
B(B_F,E_MOVE!,Instance,17,16,23,20,,?DEN?D?AENO?C);
B(B_VAROUT,,dutHomeType1.diCreepSpeed,23,18,25,20,);
B(B_VARIN,,diCreepSpeed,15,18,17,20,);
L(7,2,7,6);
L(1,2,4,2);
L(6,2,7,2);
L(7,2,17,2);
L(7,6,17,6);
L(7,10,17,10);
L(7,6,7,10);
L(7,10,7,22);
L(7,22,17,22);
L(7,14,17,14);
L(7,18,17,18);
L(1,0,1,24);
        END_NETWORK_BODY
    END_NET_WORK
    NET_WORK
        NETWORK_TYPE := NWTYPELD ;
        NETWORK_LABEL :=  ;
        NETWORK_TITLE :=  ;
        NETWORK_HEIGHT := 12 ;
        NETWORK_BODY
B(B_CONTACT,,X0_bMotorSwitch,8,5,10,7,R);
B(B_VARIN,,dutHomeType1,15,6,17,8,);
B(B_VARIN,,0,15,7,17,9,);
B(B_COMMENT,,Example for home position return,1,2,18,4,);
B(B_F,F177_PulseOutput_Home!,Instance,17,4,30,9,,?DEN?Ds_dutDataTable?Hn_iPulseOutputChannel?AENO);
L(10,6,17,6);
L(1,6,8,6);
L(1,0,1,12);
        END_NETWORK_BODY
    END_NET_WORK
END_BODY

ST body

IF DF(X0_bMotorSwitch) then
  dutHomeType1.diInitialSpeed:=diInitialSpeed;
  dutHomeType1.diTargetSpeed:=diTargetSpeed;
  dutHomeType1.diAccelerationTime:=diAccelerationTime;
  dutHomeType1.diDecelerationTime:=diDecelerationTime;
  dutHomeType1.diCreepSpeed:=diCreepSpeed;
  dutHomeType1.diDeviationCounterClearSignalOutputTime:=0;
END_IF;
(*Example for home position return*)
IF DF(X0_bMotorSwitch) then
  F177_PulseOutput_Home(s_dutDataTable := dutHomeType1, 
    n_iPulseOutputChannel := 0);
END_IF;